Thread: Extension Cord

  1. #1
    Junior Member
    Join Date
    Nov 2006
    Location
    Denver, CO
    Posts
    92
    Post Thanks / Like

    Extension Cord

    Folks
    I need to pick up a 50ft extension cord for my PC. Will a 13 AMP wire suffice or do I have to go higher?

    Thanks....

  2. #2
    Super Member
    Join Date
    Sep 2006
    Posts
    2,397
    Post Thanks / Like
    Quote Originally Posted by gandblah
    Folks
    I need to pick up a 50ft extension cord for my PC. Will a 13 AMP wire suffice or do I have to go higher?

    Thanks....
    yeah it is getting up there in length. Id go a bit higher if it were me.

  3. #3
    Super Member Al-53's Avatar
    Join Date
    Mar 2006
    Location
    Mass.
    Posts
    1,710
    Post Thanks / Like
    Go to Lowes or Home Depot and get a contractors grade extension cord...they do cost a bit more ..but with a 50' foot run it will help keep a PC or Rotary running cooler..you want at least a 12 Gauge 3 conductor cord....

    Al

  4. #4
    Super Member ScottB's Avatar
    Join Date
    Mar 2006
    Location
    South Florida
    Posts
    18,803
    Post Thanks / Like
    Quote Originally Posted by Al-53
    Go to Lowes or Home Depot and get a contractors grade extension cord...they do cost a bit more ..but with a 50' foot run it will help keep a PC or Rotary running cooler..you want at least a 12 Gauge 3 conductor cord....

    Al



    a good cord (prefessional) will last a lifetime , and long cord may not always do the trick.


    Scott

  5. #5
    Super Member Al-53's Avatar
    Join Date
    Mar 2006
    Location
    Mass.
    Posts
    1,710
    Post Thanks / Like
    Quote Originally Posted by killrwheels@autogeek


    a good cord (prefessional) will last a lifetime , and long cord may not always do the trick.

    Killler the poster was looking for a 50 footer...so I suggested he get a contractors grade with a heavier wire...12 guage or better...the heavier the wire the less draw on the PC...

    AL

  6. #6
    Super Member ScottB's Avatar
    Join Date
    Mar 2006
    Location
    South Florida
    Posts
    18,803
    Post Thanks / Like
    Quote Originally Posted by Al-53
    Killler the poster was looking for a 50 footer...so I suggested he get a contractors grade with a heavier wire...12 guage or better...the heavier the wire the less draw on the PC...

    AL

    I agree , that just grabbing a longer cord may not be the best line of attack. Grabbing a good commercial grade cord, designed for longer use is a much more valid choice. Spending a couple extra $$ is sometimes the wiser investment up front.


    Scott

  7. #7
    Junior Member
    Join Date
    Nov 2006
    Location
    Denver, CO
    Posts
    92
    Post Thanks / Like
    Thanks for the reply guys..I looked up the mini manual that came with the PC and looks like a 16 gauge is good enough upto 50 Ft...thought it's good information to share !! And for the record the PC specs are 3.7 Amps.
    The numbers below are for devices from 0-6 Amps.


  8. #8
    Super Member FloridaNative's Avatar
    Join Date
    Mar 2006
    Posts
    3,176
    Post Thanks / Like
    Good information. Thanks for putting it out there.

  9. #9
    Junior Member
    Join Date
    Nov 2006
    Location
    Denver, CO
    Posts
    92
    Post Thanks / Like
    Quote Originally Posted by gandblah
    Thanks for the reply guys..I looked up the mini manual that came with the PC and looks like a 16 gauge is good enough upto 50 Ft...thought it's good information to share !! And for the record the PC specs are 3.7 Amps.
    The numbers below are for devices from 0-6 Amps.

    This has been a learning process and as usual that involves acronyms and terminology. This might be common stuff for most people but it is new for me so putting it out here as it might benefit some others like me.

    Medium Duty -- Gauge 16 -- Max 10 Amps
    Heavy Duty -- Gauge 14 -- Max 13 Amps
    Contractor Grade -- Gauge 12 -- Max 15 Amps

    Notes:
    - Gauge and capacity are inversely proportinal - a lower gauge wire can take up more load.
    - As the length of the extension wire increases, going with a lower gauge is recommended

    Side Note
    I looked at the markings on the wire on the PC and it seems to be a Guage 16 wire and the table above recommends 16 even for a 100 ft wire. So I went one step heavier and got the 14 Gauge 50 ft extension wire as I felt contractor grade was overkill for 50 ft not to mention that the 12 gauge is quite a heavy cord.

    Thanks again for all your suggestions and inputs.

Similar Threads

  1. how to coil an extension cord
    By VISITOR in forum Tricks, Tips and Techniques
    Replies: 51
    Last Post: 04-28-2019, 09:15 PM
  2. Which extension cord?
    By RandyD in forum Auto Detailing 101
    Replies: 13
    Last Post: 06-23-2014, 07:12 AM
  3. Extension cord
    By Mercedes350 in forum Ask your detailing questions!
    Replies: 16
    Last Post: 08-09-2013, 07:34 AM
  4. Replies: 2
    Last Post: 05-17-2012, 11:44 PM
  5. Extension cord
    By Buggy Bath in forum Tricks, Tips and Techniques
    Replies: 12
    Last Post: 04-15-2012, 12:37 PM

Members who have read this thread: 0

There are no members to list at the moment.

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  

» April 2024

S M T W T F S
31 1 2 3 4 5 6
7 8 9 10 11 12 13
14 15 16 17 18 19 20
21 22 23 24 25 26 27
28 29 30 1234