You can run your Mytee HP 60 with a quality 12/3 extension cable. This is assuming you have a 20amp circuit with nothing else on it. Meaning, you can't have a blow dryer running on the same circuit.
Most homes have either a 15amp or 20amp circuit. The HP60 at maximum will have moments of draw that is close to 20amps.
You cannot use the HP60 and Flex at the same time. You may use them one at a time.
Ideally, use a 20 amp circuit and 12/3 extension cable for the HP60. Then a seperate circuit with 14/3 for the Flex.
Quote:
Originally Posted by Buggy Bath Hello, I need a new extension cord and would like your input. I plan to run my Mytee HP60 off it as well as a Flex polisher.
I want to make sure to choose the right amp and volt, etc.
Thanks. |